Arc Flash Forum
Unreasonable current during study
https://brainfiller.com/arcflashforum/viewtopic.php?f=15&t=6465
Page 1 of 1
Author:  Jake Kingsbury [ Fri Jun 26, 2026 11:26 am ]
Post subject:  Unreasonable current during study
Author:  bbaumer [ Sat Jun 27, 2026 8:22 am ]
Post subject:  Re: Unreasonable current during study
Couple of questions:
Author:  Win Engineer [ Fri Jul 10, 2026 9:11 am ]
Use the Branch fault Current data block and see what fault current you have flowing through the system. I had a model years ago that was yielding some ridiculous fault currents on a 208V system and discovered that a bunch of 10HP motors had been entered at 10,000HP. You can imagine at 208V the fault contribution from the motors! That data block showed me the fault current coming back into the bus was really high and pointed me straight to the issue.
http://www.phpbb.com/