| PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY https://brainfiller.com/arcflashforum/viewtopic.php?f=16&t=4885 |
Page 1 of 1 |
| Author: | L. Hankle [ Sat Feb 23, 2019 9:50 am ] |
| Post subject: | Re: PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY |
Since I doubt if the installer was a licensed electrician, were they at least a licensed plumber? |
| Author: | Joe Tedesco [ Sat Feb 23, 2019 1:40 pm ] |
L. Hankle wrote: Since I doubt if the installer was a licensed electrician, were they at least a licensed plumber? When I completed my inspections, I returned to my office and looked for the electrical permit and found that the installation was approved by a building inspector. I've traveled to Glendale in the past a found that property gone, and a new multistorey building in its place. |
| Author: | Jim Phillips (brainfiller) [ Sun Feb 24, 2019 3:11 pm ] |
Joe Tedesco wrote: [b]We'll discuss them as we travel through my time line as an electrical inspector in Pasadena, CA, and previously as one in New Haven, Connecticut back in the 60's. I promise we'll have some fun! I gotta lot of stories to share with you all. Looking forward to the stories from your long career serving the electrical industry. Glad you can share with us! |
| Author: | wilhendrix [ Mon Feb 25, 2019 8:56 am ] |
Back in the 1970's when I was a service electrician, I worked at an aluminum extrusion factory. This was on a reservation just south of Phoenix. This installation still stands out as one for the record book. All of the pipe was plumbing pipe including the elbows. The panel was a NEMA 1 installed outside. The panel was running at 480 volts, but was a 120/208 volt panel with typical residential level breakers. Removing the dead front revealed all white wire along with several 10 and 12 gauge wires placed directly under the main lugs. The feeders were aluminum while the #10 and 12 wire (under the same main lugs) were copper. Finally, the panel was mounted on the side of a large heat treating unit. In the summer, I'd expect that the temperatures could easily reach 180F or higher. Seeing something like this, even on the "res" was surprising. |
| Author: | bbaumer [ Mon Feb 25, 2019 11:22 am ] |
wilhendrix wrote: Back in the 1970's when I was a service electrician, I worked at an aluminum extrusion factory. This was on a reservation just south of Phoenix. This installation still stands out as one for the record book. All of the pipe was plumbing pipe including the elbows. The panel was a NEMA 1 installed outside. The panel was running at 480 volts, but was a 120/208 volt panel with typical residential level breakers. Removing the dead front revealed all white wire along with several 10 and 12 gauge wires placed directly under the main lugs. The feeders were aluminum while the #10 and 12 wire (under the same main lugs) were copper. Finally, the panel was mounted on the side of a large heat treating unit. In the summer, I'd expect that the temperatures could easily reach 180F or higher. Seeing something like this, even on the "res" was surprising. Hey, man Attachment: 220 221.jpg [ 20 KiB | Viewed 13348 times ] |
| Author: | stevenal [ Tue Feb 26, 2019 9:16 am ] |
https://www.youtube.com/watch?v=sPpHLw7KSCk&list=PL8ZTa5Hyews19Rt949Y7CjvplmTol9S6y&index=2&t=0s |
| Author: | bbaumer [ Tue Feb 26, 2019 10:29 am ] |
stevenal wrote: Jim needs to add a "like" button. |
