Arc Flash Forum
how can I detect the arc flash level at the VSD point in SKM
https://brainfiller.com/arcflashforum/viewtopic.php?f=2&t=5772
Page 1 of 1
Author:  Beca_Zion [ Sun Jan 28, 2024 3:30 pm ]
Post subject:  how can I detect the arc flash level at the VSD point in SKM
Hi,
Why SKM doesn't to detect the arc flash level at the VSD bus however it can detect the CB's bus, the bus before and the bus after VSD? is there is a way to able to detect the fault level at the VSD bus?
Author:  bbaumer [ Sun Jan 28, 2024 3:42 pm ]
Post subject:  Re: how can I detect the arc flash level at the VSD point in
Not sure I'm interpreting your question correctly but if so you can add a bus to represent the line side of the drive then connect the drive to that bus. You'll have to give the bus some enclosure properties if you don't want to use panel as the default.
Author:  Beca_Zion [ Tue Feb 20, 2024 4:44 am ]
Yes, I had to add a bus before the VSD and It worked!
I really appreciate the help.
Cheers
http://www.phpbb.com/