| Arc Flash Forum https://brainfiller.com/arcflashforum/ |
|
| Working on section adjacent to Dangerous! https://brainfiller.com/arcflashforum/viewtopic.php?f=24&t=406 |
Page 1 of 1 |
| Author: | RECS [ Mon Apr 20, 2009 4:36 pm ] |
| Post subject: | Working on section adjacent to Dangerous! |
The income section of a LV switchgear (line-side of main OCPD) has a incident energy of 65 cal/cm2 (Dangerous). The adjacent section (load side of OCPD) has a incident energy of 3 cal/cm2. The switchgear is open frame, so there is no barriers between both sections. What kind of label would you affix to this switchgear? Options: 1. Only one for the whole panels (incoming and feeder sections) with the AFIE of 65 cal/cm2. 2. Dual label, for incoming section 65 cal/cm2 and for all feeder sections 3 cal/cm2. 3. Other solution. The problem arises to be so close to a high incident energy area using only PPE of 3 cal/cm2. Thanks. |
|
| Author: | haze10 [ Mon Apr 20, 2009 5:50 pm ] |
| Post subject: | |
Without barriers you would have to use the higher rating out to an arc flash boundary that equals the lower rating. |
|
| Author: | Gary B [ Tue May 05, 2009 9:39 pm ] |
| Post subject: | |
RECS wrote: The income section of a LV switchgear (line-side of main OCPD) has a incident energy of 65 cal/cm2 (Dangerous).
The adjacent section (load side of OCPD) has a incident energy of 3 cal/cm2. The switchgear is open frame, so there is no barriers between both sections. What kind of label would you affix to this switchgear? Options: 1. Only one for the whole panels (incoming and feeder sections) with the AFIE of 65 cal/cm2. 2. Dual label, for incoming section 65 cal/cm2 and for all feeder sections 3 cal/cm2. 3. Other solution. The problem arises to be so close to a high incident energy area using only PPE of 3 cal/cm2. Thanks. According to some interpretations operating the main breaker would be illegal because you are above 40Cal/cm2. Working so close is probably no safer and could be more dangerous. |
|