Confusion when to wear PPE
https://brainfiller.com/arcflashforum/viewtopic.php?f=4&t=751
Page 1 of 1

Author:  MBSOLIS [ Tue Nov 03, 2009 1:58 pm ]
Post subject:  Confusion when to wear PPE

If the energized 480V panel has a deadfront cover and has an HRC of Cat
2 or Cat. 3, is PPE required to close or open a branch breaker?

What is your NFPA 70E interpretation?

Author:  Zog [ Tue Nov 03, 2009 2:52 pm ]
Post subject: 

MBSOLIS wrote:
If the energized 480V panel has a deadfront cover and has an HRC of Cat
2 or Cat. 3, is PPE required to close or open a branch breaker?

What is your NFPA 70E interpretation?


Yes it is, that is "interaction" with equipment. Obviously you are using the tables and should follow the HRC for that task