Arc Flash Forum
PPE to cumbersome
https://brainfiller.com/arcflashforum/viewtopic.php?f=5&t=1122
Page 1 of 1
Author:  Data Center Electrician [ Mon May 24, 2010 9:32 pm ]
Post subject:  PPE to cumbersome
Part of my job is to write procedures for vendors that perform work on their equipment. This prevents incorrect actions and unplanned events.
I have placed NFPA 70E verbage into the procedures and i ocasionally get the complaint that "this equipment will not facilitate me troubleshooting it with all that gear on. This equipment was designed before that standard and I have to troubleshoot it with long sleeves and safety glasses."
Some of the equipment has a hazard risk catagory of 3 or 4 and the technicians are checking communications and controls but they are within the boundary of the 480 volt hazard.
What have you been doing in these instances?
Author:  Zog [ Tue May 25, 2010 5:32 am ]
You are correct and they have to follow your procedures. And if something happens to a contractor on your facility you can be help liable, recently happened to IBM. I recommend using this pre-qual sheet for your vendors.
http://www.phpbb.com/