It is currently Mon Aug 17, 2026 11:18 pm



Post new topic Reply to topic
Author Message
 Post subject: SKM Unbalanced/Single Phase Module
PostPosted: Mon Dec 16, 2019 9:02 am 

Joined: Thu Jun 09, 2016 6:17 pm
Posts: 11
Good Morning All,

I am curious if anyone utilizes the SKM Unbalanced/Single Phase Module? I have several instances with single phase loads and evaluating adding this module to our current license. I am wondering if anyone could share their opinions/experiences regarding this module?

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: SKM Unbalanced/Single Phase Module
PostPosted: Mon Jan 06, 2020 1:53 pm 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 201
Location: Maple Valley, WA.
Yes, we use the Unbalanced/Single Phase SKM module. It works really well. However, if you are trying to calculate the AF energy for a single phase system less than 15 kV then you will be out of luck. The SKM AF module uses IEEE-1584 which will calculate AF energy only for a 3 phase balanced system. For open air equipment, you can use ArcPro.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: SKM Unbalanced/Single Phase Module
PostPosted: Fri Sep 04, 2020 10:43 am 

Joined: Tue Mar 05, 2019 7:37 am
Posts: 3
Location: Wisconsin
Robertefuhr wrote:
Yes, we use the Unbalanced/Single Phase SKM module. It works really well. However, if you are trying to calculate the AF energy for a single phase system less than 15 kV then you will be out of luck. The SKM AF module uses IEEE-1584 which will calculate AF energy only for a 3 phase balanced system. For open air equipment, you can use ArcPro.


You can use unbalanced/single phase to calculate AFIE results. It is an option in the Standard and Unit tab in the Arc Flash - Study Options. You must be logged into DAPPER, Arc Flash, and Unbalanced single phase to do so.

However, what it really appears to do is take one of the phase currents and uses it as a 3 phase bolted fault as a starting point to calculate AFIE. It also states per note *N24 that it is a non-3-phase bus.


Attachments:
Single Phase Arc Flash Results.jpg
Single Phase Arc Flash Results.jpg [ 93.24 KiB | Viewed 4589 times ]
Bus Report ABC Single Phase.jpg
Bus Report ABC Single Phase.jpg [ 170.4 KiB | Viewed 4589 times ]
AF Stanard and Unit Options-Single phase.jpg
AF Stanard and Unit Options-Single phase.jpg [ 85.86 KiB | Viewed 4589 times ]

_________________
Peter Van Heesch, PE
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883