This may be software-specific, maybe not. I'm modeling a multi-sectional MDP wherein a main breaker feeds subsequent sections which are open (i.e. there is no internal arc barricade from one section to the next, so an arc blast in one section will easily travel into the adjacent sections).

How would you model this in software? I'm using EasyPower, but the solution may or may not be specific to EasyPower. Normally, the software treats a "bus feeding a breaker feeding another bus" scenario as independent compartments, which is not accurate to the situation. Feel free to ask any questions you need to help flesh this out.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling different buses in same enclosure (in EasyPower
PostPosted: Mon Sep 08, 2025 8:45 am 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 60
Here are two photos illustrating what I'm talking about; one is the gear which is internally open, and the other shows the busing on the load side of the breaker passing into adjacent equipment.

Also note that there is no physical barricade between the line and load sides of the main breaker, and the opening between sections extends from the floor to the top of the cabinets.


Attachments:
IMG_2463.JPG
IMG_2463.JPG [ 5.32 MiB | Viewed 769266 times ]
IMG_2445.JPG
IMG_2445.JPG [ 3.72 MiB | Viewed 769266 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling different buses in same enclosure (in EasyPower
PostPosted: Mon Sep 08, 2025 11:49 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 182
Can you model as one bus since it's not sectionalized any way?

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling different buses in same enclosure (in EasyPower
PostPosted: Mon Sep 08, 2025 12:26 pm 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 60
mpparent wrote:
Can you model as one bus since it's not sectionalized any way?

Mike

It's not sectionalized, but there is a main breaker with both line and load side busing.

Are you suggesting I model it as one bus only for the incident energy calculations? like creating a separate scenario specifically for the calorie calcs?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling different buses in same enclosure (in EasyPower
PostPosted: Tue Sep 09, 2025 6:19 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 182
I am suggesting model as a single bus. In my opinion, line load side bus is irrelevant. Include your main/feeder breakers per field observations.

Mike


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883