It is currently Wed Jun 24, 2026 8:59 pm
 Post subject: Work in Junction Boxes and Troughs
PostPosted: Fri Oct 23, 2020 8:53 am
Good Morning,
Has anyone required arc rated PPE for work in junction boxes or troughs with no exposed live parts, but has energized insulated conductors? What if a split bolt is not taped up well, or a wire nut falls off....? I know my opinion, but was curious if anyone else has run into this discussion with their employees or employer.
 Post subject: Re: Work in Junction Boxes and Troughs
PostPosted: Mon Oct 26, 2020 7:43 am
I have seen a fair number of electricians put on voltage rated gloves and protective gloves when handling wiring in a pull/junction box. Although I haven't seen a written practice for it, I think the use of voltage rated gloves is good practice.
PostPosted: Mon Oct 26, 2020 12:41 pm
Risk assessment needed based on task.
Mike
PostPosted: Mon Oct 26, 2020 4:24 pm
Hi All, As an electrician, my first thought is what is the voltage system- single phase, 3 phase, etc? How does the junction box or trough present? Age and condition? Have I been here before and know something about the installation, etc? You mentioned that we have insulated conductors and wire connectors. However pending on who was there last, we may have a wire connector come off leaving an exposed connection when moving the wires apart perhaps. Regardless of the voltage system, I would likely don a pair of rubber insulated gloves with leather protectors. At least some protection from shock and those gloves can offer very good protection from at least the heat if a short circuit was to occur and resulting in a flash. Likely may not go with hte hard hat faceshield and balaclava as it may be more combersome and restrictive pending on the location. As mentioned below some form of a risk assessment.
I hope that this is of some help
All the Best
PostPosted: Tue Oct 27, 2020 11:27 am
This would be similar to an electrical manhole. If requested, an arc flash label could be installed, as if the conductor was a splice point or a termination. If there were multiple voltages/circuits in the enclosure a label could be developed for the worst-case shock and arc flash levels.
PostPosted: Wed May 20, 2026 12:28 am
Leonard wrote:
Hi All, As an electrician, my first thought is what is the voltage system- single phase, 3 phase, etc? How does the junction box or trough present? Age and condition? Have I been here before and know something about the installation, etc? You mentioned that we have insulated conductors and wire connectors. However pending on who was there last, we may have a wire connector come off leaving an exposed connection when moving the wires apart perhaps. Regardless of the voltage system, I would likely don a pair of rubber insulated gloves with leather protectors. If you’re just looking to unwind, Win casino onlayn kazino can be a simple way to relax for a bit. At least some protection from shock and those gloves can offer very good protection from at least the heat if a short circuit was to occur and resulting in a flash. Likely may not go with hte hard hat faceshield and balaclava as it may be more combersome and restrictive pending on the location. As mentioned below some form of a risk assessment.
All the Best
agree with this — too many unknowns once you open it up, gloves are a pretty reasonable baseline even if everything looks insulated