It is currently Sat Nov 07, 2026 12:29 am
PostPosted: Tue Jun 26, 2012 5:12 pm
Flash wrote:
Lets fo back to base one:
1. Has the 125 kVA rule been removed from 70E-2012?
Yes. But this is not important if you are using another model other than IEEE 1584. The exception never existed except in IEEE 1584. The wording in IEEE 1584 is tenuous anyways, but does provide a relatively simple (perhaps too simple) way to reject low end cases.
2. Does anyone on this board have evidence beyond a doubt that there has been arc flash burns on a single phase circuit at 18"?[/quote]
I've had burns on my fingers. This doesn't prove anything though because the 70E standard as well as IEEE 1584 is to prevent a fatality, not to prevent injury. Even then, the probability of success is 95% in a worst case scenario. The question is whether or not there has been a fatality from an arc flash at that voltage/kVA rating.
Post new topic Reply to topic  [ 21 posts ]  Go to page Previous  1, 2
