It is currently Sat Nov 07, 2026 6:29 pm
 Post subject: Lexan cover over main disconnect and fuses
PostPosted: Tue Jul 29, 2008 11:19 am
Is lexan over main disconnect and fuses a good idea for industrial panels ranging from 30 amps to 400 amps. If an arc flash were to occur at the main disconnect what happens to the lexan. Does it become a projectile, a molten mass of plastic or will it help protect personnel?
Bill
PostPosted: Tue Jul 29, 2008 3:09 pm
I would think that any non-conductive cover that would help prevent inadvertent contact with the body or tools would help. I would also think that hot plastic shouldn't be as bad as copper or stainless steel. After all, the extra barrier just might keep someone from making that mistake.
Alan
PostPosted: Wed Jul 30, 2008 6:24 am
I agree with Alan but have to add, you dont really know what will happen to the barrier. As far as your arc flash calcs and PPE selection, pretend it is not there.
PostPosted: Wed Jul 30, 2008 4:43 pm
Absolutely
I started to add that no barrier protection should be considered but figured that is was just to be used for extra protection from contact. Also thought that it was a good idea since it is clear, you can still see what is there. How about drilling some small holes so it does not need to be removed for voltage tests?
Alan
PostPosted: Fri Aug 01, 2008 3:54 am
thanks Alan
PostPosted: Fri Aug 01, 2008 3:56 am
Thanks for the input.
