| Author |
Message |
wbd
Post subject: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Sat Dec 20, 2014 6:48 am |
| Plasma Level |
Joined: Wed May 07, 2008 5:00 pm Posts: 881 Location: Rutland, VT
| Attachments: |
_________________ Barry Donovan, P.E. www.workplacesafetysolutions.com
| Top |
dinkelja
Post subject: Re: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Mon Dec 22, 2014 9:23 am |
A few questions about your IE calculation: Are you calculating the incident energy at the load side of the breaker, line side, or transformer bushings? What gap distance did you use? What is the XF primary protection mechanism / type?
| Top |
lovetacycle
Post subject: Re: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Tue Dec 23, 2014 6:56 am |
| Top |
wbd
Post subject: Re: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Tue Dec 23, 2014 8:48 am |
| Plasma Level |
| Top |
PaulEngr
Post subject: Re: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Sun Dec 28, 2014 9:15 am |
| Plasma Level |
Joined: Tue Oct 26, 2010 9:08 am Posts: 2178 Location: North Carolina
| Top |
wbd
Post subject: Re: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Sun Dec 28, 2014 9:48 am |
| Plasma Level |
| Top |
ekalbs4
Post subject: Re: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Mon Dec 29, 2014 10:15 am |
Joined: Wed Jun 24, 2009 4:45 pm Posts: 41 Location: WA State
wbd wrote: True on the risk assessment. Items to consider is bare lugs on breaker exposed and phase spacing close, so what happens when opening the doors scatters mice up the cable to across the breaker lugs? Far fetched but in realm of possibility, I think. Can you somehow cover the bare lugs, or at least discourage the possibility of a rodent bridging between phases? The idea of a rodent causing a problem when opening a cabinet door has been an ongoing area of discussion at my utility. OSHA's 1910.269 Appendix E, Assessment Guidelines, says the following, "The Occupational Safety and Health Administration will consider an employee exposed to electric-arc hazards if there is a reasonable likelihood that an electric arc will occur in the employee's work area, in other words, if the probability of such an event is higher than it is for the normal operation of enclosed equipment." To me, the key to this statement is "if the probability of such an event is higher". Many people seem to think that the probability of an event is increased because a rodent is scared by the opening of a door. Personally, I'm not convinced that this is true and believe that maybe the probability is the same or even reduced. A rodent inside a cabinet would have already explored the entire contents and been at risk of a problem on a daily basis while the door was closed, so I don't believe the probability goes up. It might even be less since a scattering rodent is likely to retreat down, away from energized parts.
| Top |
PaulEngr
Post subject: Re: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Tue Dec 30, 2014 5:11 pm |
| Plasma Level |
| Top |
lebd01
Post subject: Re: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Fri Jan 09, 2015 7:01 am |
Daniel Lebeau, eng.
| Attachments: |
| Top |
jcwhite01
Post subject: Re: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Tue Feb 17, 2015 3:10 pm |
Thanks!
| Top |
PaulEngr
Post subject: Re: Circuit Breaker in Pad Mount Transformer Cabinet Posted: Tue Feb 17, 2015 8:18 pm |
| Plasma Level |
| Top |
Page 1 of 1
[ 11 posts ] |