 Post subject: Determining Capacitance of 3-Phase Capacitor Banks
PostPosted: Tue Aug 18, 2020 4:25 pm 

Joined: Tue Aug 18, 2020 3:14 pm
Posts: 10
Hello,

I have a very basic question on how to determine the capacitance for a 3-Ph capacitor bank.

If I am not mistaken this is done using the following equation:
Capacitor Reactance = kV^2/Mvar
Terefore Capcitance= 1/ (Xc*2*pi*60)

Where:
Mvar is the power is in Mvar
Vrms is the rms voltage Line to Line Voltage in kV
Freq is the frequency in Hz
Capacitance is in farads

Now if the equations above using the following sample nameplate data:
10 kVar @ 480 Volts for a 3Ph bank.
Attachment:
Eaton1.jpg
Eaton1.jpg [ 211.82 KiB | Viewed 16926 times ]


Xc= (0.480)^2 / (10kVar/1000) = 23.04 ohms
Therefore Capcitance= 1/ (Xc*2*pi*60) =0.000115129 Farads or 115.129 uF

Are the results above the per phase or the total 3-Ph reactance and capacitance of the bank?


Also how would the calculation above change for a bank made up of multiple capacitors?
For example in the case below where 8 capacitors make up the capaitor bank.
Attachment:
Multi_Eaton2.jpg
Multi_Eaton2.jpg [ 228.03 KiB | Viewed 16926 times ]


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Determining Capacitance of 3-Phase Capacitor Banks
PostPosted: Mon Aug 24, 2020 7:50 am 

Joined: Mon May 18, 2020 8:42 am
Posts: 2
Instead of giving you a direct answer, can I suggest you do a similar calculation for a three-phase 100kW 480V resistor. Is your answer for a single-phase or the total resistance?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883