It is currently Thu Oct 08, 2026 6:26 am
 Post subject: 12 Pulse VFD Short-Circuit and Arc Flash Calculations
PostPosted: Thu May 12, 2022 6:22 am
Hi,
When modeling a 12-Pulse VFD that is fed from multiple transformers or a single multi-winding transformer, is it common to only utilize the fault current from one of the two transformers/windings? If the VFD input sources are within the same enclosure, should a scenario be considered where a fault could propagate from one source to the other and both sources of fault current should be considered?
Thanks for the input.
 Post subject: Re: 12 Pulse VFD Short-Circuit and Arc Flash Calculations
PostPosted: Tue Nov 01, 2022 4:01 am
Hi,
Anyone have any input or guidance regarding this?
PostPosted: Wed Nov 02, 2022 1:37 pm
Same enclosure and no barriers? Yes, I would consider a fault involving both sources.
