It is currently Sat Oct 24, 2026 2:55 am
 Post subject: Calculate %Z autotransformers in open delta?
PostPosted: Tue May 05, 2015 7:44 am
I have two single phase 480V-120V 75KVA 5.0% Impedance transformers, 625A secondary.
They are connected as boosting autotransformers in open delta, 480V primary, 600V secondary.
I need to calculate fault current on the secondary.
The equivalent transformer capacity would be 625A x 600V x1.73 = 469KVA
But I'm not sure how to calculate the equivalent impedance.
Any direction to reference material or a mathematical method is appreciated. I am not in a position to physically measure impedance by shorting the secondaries and varying input voltage.
gary
 Post subject: Re: Calculate %Z autotransformers in open delta?
PostPosted: Tue May 05, 2015 9:41 am
Correction:
Equivalent KVA = (75+75) x2 x.86 = 258KVA
PostPosted: Mon May 11, 2015 10:02 am
check out:
http://forums.mikeholt.com/showthread.php?t=126891
