It is currently Mon Nov 23, 2026 1:42 pm
 Post subject: MCC Modeling
PostPosted: Thu Oct 09, 2025 10:09 am
Hello - any videos or articles or help yall can proivde to help model an MCC? I have an MCC Im modeling with both VFDs and FVNRs, do we model these or ignore them? See image for diagram of MCC
 Post subject: Re: MCC Modeling
PostPosted: Mon Oct 13, 2025 1:21 pm
I modeled the bussing of the MCC based on the incoming lugs. I never tried to model each individual bucket, too much work and not enough barriers between them and the vertical bussing. Labels went on the vertical wireway doors. Putting labels on each bucket is information overload and they will likely be ignored.
The only exception would be for the larger MCCs where the main device was actually in a separte section and the cross bussing was at the top of the structure.