I’m working on a fault current calculation for a meter stack and had a question regarding series ratings.

According to the manufacturer, the Siemens QPH breaker can be series-rated with a Siemens 3VA6-H breaker, resulting in a load center feeder breaker with a 100kA AIC rating. Additionally, a Siemens QP breaker can be series-rated with a QPH breaker at 22kA.

My question is: if the feeder breaker (QPH) is part of a series combination rated at 100kA with the upstream 3VA6, can the downstream branch breakers (QP) also be considered as having a 100kA series rating? Or are they still limited to their own tested series rating (22kA with QPH)?


Attachments:
Screenshot 2026-04-02 110739.png
Screenshot 2026-04-02 110739.png [ 20.04 KiB | Viewed 15056 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Meter Center Series Ratings
PostPosted: Fri Apr 03, 2026 4:07 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
75kA available looks pretty high but not enough info to really evaluate. Are you confident in that value?

Also what Mike said RE: series ratings. Eaton has some info on tenant rating like what you have there with 3 breakers but the answer is what Mike said. You might be ok if the QP also has a rating with the 3VA6 but you'll need to look it up.

From Eaton. Siemens may be different:

Attachment:
Screenshot_20260403_071041_Chrome.jpg
Screenshot_20260403_071041_Chrome.jpg [ 712.14 KiB | Viewed 14987 times ]

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883