It is currently Wed May 13, 2026 5:12 am



Post new topic Reply to topic
Author Message
 Post subject: SKM "Fed From"
PostPosted: Tue May 12, 2026 10:13 am 

Joined: Fri Jan 09, 2026 1:59 pm
Posts: 4
Hello,

I'm trying to print labels in SKM and the client wants it to say Fed from: "upstream bus" basically what panel or disconnect or what it is fed from. However, in all of my attempts, all I've been able to get to show is the protective device that is clearing the fault. I don't even necessarily need to print from within SKM I'm willing to print from one of the external software's, I just need some way (preferably not by hand) of capturing the upstream bus that is feeding the bus that the label is going on.

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: SKM "Fed From"
PostPosted: Tue May 12, 2026 2:03 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 492
Location: Indiana
This may or may not work for you but I name breakers PANELBOARD NAME LOAD SERVED.

For example, MDP feeds panels A, B, C and D. MDP also has a main breaker. My breaker names for panel MDP are therefore:

MDP MCB
MDP A
MDP B
MDP C
MDP D

That way the Fed From or Protected By field on the label will show the panel and breaker both, MDP A for example.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: SKM "Fed From"
PostPosted: Tue May 12, 2026 2:05 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 492
Location: Indiana
Here's a video on using SKM label designer just in case:

https://youtu.be/x1TT7UHxf2E?si=dAB4Vdci4yehZUA7

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: SKM "Fed From"
PostPosted: Wed May 13, 2026 3:16 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 492
Location: Indiana
This is what I was trying to describe:

Attachment:
PARTIAL ONE-LINE.jpg
PARTIAL ONE-LINE.jpg [ 358.77 KiB | Viewed 15 times ]


Attachment:
NAMES ON LABEL.jpg
NAMES ON LABEL.jpg [ 591.22 KiB | Viewed 15 times ]

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883