It is currently Sun Nov 15, 2026 7:00 pm
What is the highest DC voltage that you/clients have?
Less than 50V 14%  14%  [ 5 ]
50-600V 41%  41%  [ 15 ]
601-1500V 32%  32%  [ 12 ]
Greater than 1500V 8%  8%  [ 3 ]
No DC systems 5%  5%  [ 2 ]
Total votes : 37
 Post subject: Highest DC Voltage
PostPosted: Sat May 22, 2021 6:52 am
DC voltage continues to be a topic of discussion. Especially areas of higher DC voltage. This week's question is simple:
Less than 50V
50-600V
601-1500V
Greater than 1500V
No DC systems
 Post subject: Re: Highest DC Voltage
PostPosted: Sat May 29, 2021 4:20 am
Actually if you have inverters and 460V in your plant, you have 650+ VDC in your inverter. Most inverters have either the DC bus or the DBR terminals brought out to the terminal strip.
When I was at Parker, we actually used common bus systems. I had several drives in my cubical for assisting customers with product support, and I supplied 460V to one drive and powered up 2 others using that drive's DC Bus. Most drives I did not run a motor on them and only connected to the drive to troubleshoot the customers' configuration problems.
