| Author |
Message |
Jim Phillips (brainfiller)
Post subject: Ever have an electrical fire? Posted: Sun Mar 26, 2017 2:59 pm |
| Plasma Level |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1738 Location: Scottsdale, Arizona
No Yes – stories are certainly welcome.
| Top |
bbaumer
Post subject: Re: Ever have an electrical fire? Posted: Mon Mar 27, 2017 3:15 am |
| Arc Level |
I saw a heat detector catch on fire during testing once. Does that count? We were doing a new fire alarm system acceptance test. We don't use magnets. We test smokes with smokes and heats with heats etc. We had one of those cup style testing poles over this detector. It was taking an unusually long time to go into alarm. I looked up at the transparent cup and saw a glow inside. Yikes! Attachment:
_________________ Retired but I might visit once in awhile
| Top |
willcoc
Post subject: Re: Ever have an electrical fire? Posted: Mon Mar 27, 2017 5:41 am |
Joined: Fri Jul 10, 2009 10:14 am Posts: 32 Location: West Central, OH
| Attachments: |
| Top |
Larry Stutts
Post subject: Re: Ever have an electrical fire? Posted: Mon Mar 27, 2017 6:06 am |
| Sparks Level |
Joined: Tue Apr 17, 2012 8:19 am Posts: 253 Location: Charlotte, NC
Yes,
| Top |
Scott Peterson
Post subject: Re: Ever have an electrical fire? Posted: Mon Mar 27, 2017 8:32 am |
I work in a woodworking factory. On two separate occasions I had motors catch fire right as I was standing there. These were open drip proof type motors, and when they failed electrically they shot sparks out of the open vents in the rear of the motor. We keep things pretty clean here, but if they had landed in a pile of dust and no one was standing there, there would have been a fire. Now we ONLY use TEFC motors, which are much less likely to do this. Another time I was visiting another wood shop when an employee was sweeping next to a large dust collector. He bumped into a piece of flexible armored conduit, which shorted internally made a big flash, and burned a row of holes in the flex conduit. It was not the waterproof plastic sealed type, just metal. This was a 15 hp unit with an 100 amp service. The wires had vibrated for years inside the conduit until the insulation was worn through. Bumping the conduit with the broom caused the wire to short to ground. Amazingly there was no injury or fire, partly due to a clean concrete floor and brick wall nearby.
| Top |
PaulEngr
Post subject: Re: Ever have an electrical fire? Posted: Mon Mar 27, 2017 9:39 am |
| Plasma Level |
Joined: Tue Oct 26, 2010 9:08 am Posts: 2178 Location: North Carolina
| Top |
wilhendrix
Post subject: Re: Ever have an electrical fire? Posted: Wed Apr 12, 2017 9:26 am |
Does an older 480 volt 3000 amp MCC and distribution count? If so, then my answer is yes. In the late 70's I was a brand new service electrician, that meant working alone for commercial and industrial customers. It was late Friday afternoon in the middle of summer in Phoenix. I got paged (no cell phones then) to go to a tannery. The tannery was 50 miles away from where I was. I got there as fast as I could because the client said, "the power is off and we have a hundred thousand dollars of hides that are rotting!" I arrived and found they had a utility but the client had shut off their 3000 amp fused main. BTW, no GFI at this time.
What caused the fault? Here's what probably happened. The gear was made before it was common practice to plate the copper buss. This bare copper buss was exposed to the chemicals the tannery used to "unhair" the hides. The copper was attacked by the chemical and over the years, the copper flaked off. Instead of falling harmlessly on the concrete slab, it fell onto spider webs in the gear. The web was strong enough to hold the copper and it created a high resistance path between phases. I made several mistakes, but chiefly, I allowed this emergency to override my good judgement. I could have driven back to Phoenix and gotten the Megger., I could have been much more careful about trying to see inside the gear. I could have even substituted a smaller fuse in the disconnect. But I did none of those things. Lucky, no one was injured, only equipment damage and loss of production. So, what's to be learned from my mistakes? Mainly that you not let an emergency override you judgement and ignore safe work practices. Behave like the professional you are. The time taken to think through your next moves might be more than worth it. Particularly if it prevents any injury.
| Top |
Page 1 of 1
[ 7 posts ] |