 Post subject: incident energy calc
PostPosted: Thu Jul 30, 2026 4:32 am 

Joined: Thu Dec 18, 2025 3:21 pm
Posts: 22
how is it that at 1000 INST the level is 1, but if INST is 1200 it jumps to level 3? worst case arcing fault is 4005A so I assume anything under this and it trips instaneously. no other sources or motor loads in the circuit


Attachments:
3.png
3.png [ 10.02 KiB | Viewed 19548 times ]
2.png
2.png [ 83.64 KiB | Viewed 19548 times ]
1.png
1.png [ 90.19 KiB | Viewed 19548 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: incident energy calc
PostPosted: Thu Jul 30, 2026 5:21 am 

Joined: Mon Jul 27, 2026 8:58 am
Posts: 7
Take a look at your arcing fault numbers...

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: incident energy calc
PostPosted: Thu Jul 30, 2026 8:06 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Protective device clearing time defines the arc duration. Elaborating on what mparenteau stated, the device clearing time is a function of the arcing fault current and devices time current curve. The clearing time has the largest effect on the incident energy. i.e. clearing time doubles = incident energy doubles. Also, IEEE 1584 has an arcing current variation factor so if the arcing current is slightly to the right of the instantaneous, the adjustment could push it just to the left resulting in a longer duration.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: incident energy calc
PostPosted: Thu Jul 30, 2026 12:15 pm 

Joined: Thu Dec 18, 2025 3:21 pm
Posts: 22
mparenteau wrote:
Take a look at your arcing fault numbers...

Mike


I did look at the arcing fault, both values are to the right of the INST settings. So I was thinking it should trip, but as Jim mentioned below it may be due to the tolerance used not only in the equations, but in the breaker characteristics as well. This one in particular shows =-20%


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: incident energy calc
PostPosted: Thu Jul 30, 2026 12:25 pm 

Joined: Thu Dec 18, 2025 3:21 pm
Posts: 22
Jim Phillips (brainfiller) wrote:
Protective device clearing time defines the arc duration. Elaborating on what mparenteau stated, the device clearing time is a function of the arcing fault current and devices time current curve. The clearing time has the largest effect on the incident energy. i.e. clearing time doubles = incident energy doubles. Also, IEEE 1584 has an arcing current variation factor so if the arcing current is slightly to the right of the instantaneous, the adjustment could push it just to the left resulting in a longer duration.


Is there a way to determine what SKM is using for the arcing current? Because I still don't see why its not tripping even at 1200A INST


Attachments:
4.png
4.png [ 41.64 KiB | Viewed 19515 times ]
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883