It is currently Fri Nov 06, 2026 8:50 pm
 Post subject: IEEE 1584 ranges models
PostPosted: Sun Jul 13, 2014 8:57 pm
Section 5.1 of IEEE 1584 defines the voltage range as below:
[*]Voltages in the range of 208 V–15 000 V, three-phase.
Does it means phase to phase voltage or phase to ground voltage? I understand that single phase arc quickly evolves into three-phase arc per IEEE model but does it true single phase to ground mean phase to ground voltage? If that is a case, then 25kV system with single phase to ground less than 15kV would be appropriated to apply IEEE 1585 instead of Arcpro which conflicts with OSHA software recommendation.
 Post subject: Re: IEEE 1584 ranges models
PostPosted: Mon Jul 14, 2014 4:27 am
That is the 3 phase voltage which is phase to phase to follow convention.
Not sure what you are asking here. Please clarify.
This is a moot issue since it is answered above as it is 3 phase voltage and would fall into the More than 15 kV column in OSHA Appendix E Table 3.
PostPosted: Mon Jul 14, 2014 6:03 pm
By definition, an electric arc is a visible plasma discharge between two electrodes that is caused by electrical current ionizing gasses in the air
Varc < 15kV between two un-grounded conductors
25kV nominal voltage system with single phase to ground arcing ==> Varc < 15kV between un-grounded and grounded conductors
I understand the technical wording but my gut didn't feel the same.
