It is currently Thu Nov 05, 2026 10:39 am
 Post subject: Incident Energy - 30A Disconnect
PostPosted: Wed Nov 21, 2018 12:05 pm
Has anyone come across incident energy over 8 cal for a 30A 480V disconnect?
 Post subject: Re: Incident Energy - 30A Disconnect
PostPosted: Thu Nov 22, 2018 7:53 am
It can happen.
Since the arc duration is usually defined by how long it takes an upstream overcurrent device to clear the arcing current, a larger incident energy is often due to a longer clearing time from that device.
What device is upstream? Do you have a clearing time from the study result?
PostPosted: Fri Nov 23, 2018 10:12 am
Easier than that if it's fed by one big transformer like say a 1000 kva.
PostPosted: Mon Nov 26, 2018 8:50 am
we have it happen quite often in our Quarries. When you go 1500 feet of cable to a pump down in the pit the short circuit current goes low and the trip time on the Circuit breaker becomes long.
PostPosted: Tue Nov 27, 2018 12:57 pm
Typically happens at test switches or switches for power factor correction (or PQ monitoring) that are tapped off the main bus of 480 V switchgear. Why those switches are installed the way they are is another topic. ;) As many have pointed out, it's what's upstream that matters.
PostPosted: Wed Dec 05, 2018 8:50 pm
The question would be more interesting if we discussed the possibility of exceeding 1.2 cal down stream from a 30A or 60A fuse and or breaker. For those that use arc flash software try and get the incident energy above 1.2 cal down stream from a Mersen A6K200R or Buss KTSR200.
PostPosted: Mon Dec 10, 2018 6:58 pm
That seems to be the case regardless of the make or model of device once you get down below about 150%.
