arcflash71 wrote:
If there is a fault in the differential zone, both the Unit breaker and the field breaker will open. Is there an accepted method to account for the Unit fault contribution while the field collapses and the machine spins down? Is this fault contribution significant?
I don't know of an "officially recommended" method, but what I have managed to do for our large motors and generators is to model and graph the decrement curve. You can then either use this decrement curve directly, and integrate it for the total arc flash energy, or, as I did, approximate it. For the majority of the generators that we have, which are probably significantly smaller then yours, I found that by assuming 100% fault contribution for 10 cycles, then decreasing to 100% of full load current for the remaining time, I achieved a pretty good approximation of the total energy available. And yes, this fault contribution can be significant, especially for large generators and motors.