 Post subject: NFPA 70E - 130.7 Personal and Other Protective Equipment
PostPosted: Thu Dec 08, 2011 8:20 am
OK, the 2012 edition of NFPA 70E just added to the confusion. As I recall, the 2009 edition added "interaction" as a possible arc flash hazard. They added language in a few places and it is still in there.
Now we have a new Informational note No. 2 that states:
"normal operation of enclosed electrical equipment operating at 600 volts or less, that has been properly installed and maintained by qualified persons is not likely to expose the employee to an electrical hazard.
Does this mean operating a breaker or racking in / out a breaker on new equipment that has been tested and is in good / new condition is not a possible arc flash hazard? I think this new note just added to the confusion.
Doesn't this new note also contradict the on going debate about doors open vs. doors closed. i.e. operation of enclosed equipment... ...properly installed ..... not likely to expose to hazard... etc.
PostPosted: Thu Dec 08, 2011 8:43 am
It does add to the confusion, and "properly installed and maintained " is open to interpretation as well, even safety related switchgear at nuclear plants experiences failures and arc flash events (Here is a recent one) and those breakers are more "properly installed and maintained " than anything else at any other facility.
PostPosted: Sat Dec 10, 2011 5:51 pm
Opening/closing: Yes. And the installed/maintained part is very easy to answer. See the next major section which details specific detailed requirements for maintenance; specifically 70B and/or NETA MTS. Unfortunately in reality neither of these is very realistic either and needs work, but those are the only two general standards out there I'm aware of. For molded case circuit breakers the "bible" is NEMA AB4 which is available free from NEMA. IEEE Gold Book has extensive data on failure rates and cursory examination shows that with some careful consideration of possible failure modes, dangerous (arcing) failures are at least 10^-4 or 10^-5 or less under those circumstances, which is suffficiently low enough that most risk assessment procedures consider it acceptable risk.
Not at all. It simply document's the 70E Technical Committee's position. The additional notes under the arc flash analysis section plus the section describing required maintenance together clearly indicate the position as to acceptable maintenance practices. Properly installed is pretty straightforward as well since that is described in the NFPA 70 section as well as the requirements in NFPA 70E (coordination, AIC/SCCR, etc.).