It is currently Tue Oct 27, 2026 1:44 am
Have you ever experienced nuisance tripping from a GFCI device?
Yes 83%  83%  [ 19 ]
No 17%  17%  [ 4 ]
Total votes : 23
 Post subject: GFCI Devices Nuisance Tripping
PostPosted: Sun Jul 22, 2012 6:03 am
Class A ground fault circuit interrupters (GFCI) are designed for the protection of personnel. NFPA 70E addresses GFCI requirements in more detail with the 2012 Edition.
This week's question:
  • Yes
  • No
PostPosted: Sun Jul 22, 2012 9:05 am
Do you mean it was a nuisance that the GFCI did its job, or the reason for the GFCI trip was never determined?
PostPosted: Sun Jul 22, 2012 4:27 pm
Thanks JBD - I believe I need to clarify this a bit more. I meant nuisance tripping from normal operations such as starting a device like a saw, hair dryer etc. i.e. as you stated, the reason was never determined.
Sometimes when a motor operated device is on a GFCI circuit, the initial magnetizing current during starting (not the locked rotor current) can cause the GFCI to see enough of an unbalance that it nuisance trips. I have had several nuisance trips over the years with power tools on a GFCI circuit tripping. It is not a common occurrence but it does happen.
PostPosted: Mon Jul 23, 2012 5:22 am
Beard trimmer in my bathroom.
Haven't felt any shock, so reset the GFCI and restarted the trimmer without any other incident.
