It is currently Fri Oct 30, 2026 9:00 am
Do you (people you know) maintain the correct working distance when performing energized work?
Yes 31%  31%  [ 19 ]
No 5%  5%  [ 3 ]
We Try - not always possible 48%  48%  [ 30 ]
We don't perform energized work 16%  16%  [ 10 ]
Total votes : 62
 Post subject: Maintaining Correct Working Distance
PostPosted: Sun May 12, 2013 1:41 pm
The prospective incident energy used to define PPE requirements is based on the worker’s chest and head being a fixed distance away from the arc known as the working distance. Both NFPA 70E and IEEE 1584 reference this distance.
Here is this week’s question:
  • Yes
  • No
  • We Try - not always possible
  • We don't perform energized work
PostPosted: Mon May 20, 2013 8:27 am
It would seem the correct working distance is something the engineer chooses when performing a study and determining energy for PPE at that distance, and not something a tradesman has much discretion over. It is understood that if PPE is chosen for 18" distance and one's hands are closer than that; the protection may not be sufficient.
PostPosted: Wed May 29, 2013 5:40 pm
I don't have the reference at hand, but I believe the working distance is for face/torso/neck.
