It is currently Mon Aug 31, 2026 1:09 am
 Post subject: kWh Meter Work
PostPosted: Tue Jan 06, 2009 8:43 am
What is everyone doing for replacing/pulling/seal out of residential kWh meters?
Are you requiring a minimum of 4 cal clothing? What other PPE (face shield)?
What about the 480V metering that is not instrument PT fed?
PostPosted: Fri Jan 09, 2009 10:00 am
The NESC Work Rules subcommittee is proposing new tables for section 41 for voltages below 1000 volts and currents below 50,000 amps.
Below is a summary of a relevant part of the proposed table
Self-contained meters /
Pad-mounted transformers / Panels and Cabinets
251 – 500 V
20 cal/cm^2(note 4)
4. Industry testing on 480V equipment indicates exposures for self-contained meters do not exceed 20 calories/cm2.
