It is currently Sat Oct 24, 2026 3:07 am
 Post subject: 2009 NFPA 70E errors - how to report them
PostPosted: Fri Jan 23, 2009 1:15 pm
I was just comparing the NFPA 70E (2009) to Canadian Z462-08 and noticed that in the NFPA 70E on page 70E-25, in Table 130.2(C), the "Restricted Approach Boundary (column (4)) that many of the metric distances are incorrect. Someone made an error when converting from feet/inches to meters or mm.
The Z462-08 is correct in all of their conversions (see Dec 08 Z462-08 page 34, Table 1).
The NFPA 70E is wrong.
PostPosted: Sat Mar 07, 2009 8:18 am
Mark,
As we discussed on the telelphone, you are correct, there are a few numbers that are off a bit. I checked with one out at our last 1584 meeting and it was suggested that you or someone submit a proposal to change it in the next Edition of 70E. That's about the only way to make sure it is addressed.
Good Catch!
PostPosted: Thu Mar 12, 2009 6:34 am
There is an errata for NFPA 70 E 2009 on the NFPA web site. The print-out I have says please see http://www.nfpa.org/codelist.
