For my understanding of this tables:
It is used some kind of distance from arc:"Calculated by using minimum approach from Table 441-2 and subtracting two times the assumed arc gap length"
Does this mean that for instance the 161 to 169 kV calculation is done wirth the following input:
Ik= 20kA(assumed single phase)
Arc Gap distance 161kV/10=16.1 inch
Distance to gap: (From table 441-2): 51 inches(10ft3inch,use T=3)-2*16.1 inches=19 inches
If I do calculation with arcpro(is was told that this tables where made by using arcpro?), input shown in picture. I get a result of 11.9 cal/cm2 and not 4cal


Attachments:
c2picture.JPG
c2picture.JPG [ 14.37 KiB | Viewed 2311 times ]
arcpro_quest.JPG
arcpro_quest.JPG [ 26.45 KiB | Viewed 2311 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Question about table 410-2 ieee.c2. vs arcpro
PostPosted: Thu Mar 15, 2018 8:27 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
The table uses line to line voltage, but when finding arc length the note 1 says to divide the line to ground kV by 10. Your calculated arc gap should be divided by sqrt(3).

When I've looked at this in the past, I found the tables did not necessarily correspond to the MADs in the same revision of the NESC. Looking back a revision or two produced better results.

Why 9.3 cycles? Tabulated value is 11.9.

Might try changing the electrodes; I forget which gave better results.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883