It is currently Sun Oct 18, 2026 3:57 am
Would you use an IEEE single phase arc flash model/equations?
Yes 49%  49%  [ 18 ]
No 35%  35%  [ 13 ]
Not Sure 16%  16%  [ 6 ]
Total votes : 37
 Post subject: Need for Single Phase Arc Flash Model
PostPosted: Sun Aug 18, 2019 4:10 pm
IEEE 1584 is valid for three phase arc flash calculations only.
This week’s question is about a need for a single-phase model/equations.
Would you use an IEEE single phase arc flash equations/model?
Yes
No
Not Sure
 Post subject: Re: Need for Single Phase Arc Flash Model
PostPosted: Mon Aug 19, 2019 4:37 am
I voted "not sure" We could use it but sometimes have difficulty covering all 208 volt so moving further into single phase would be quite an undertaking.
PostPosted: Thu Sep 19, 2019 12:57 pm
For electric utility Arc-Flash Analysis, I use ArcPro for single-phase analysis per OSHA 1910.269, Appendix D, Table 3, and only use the IEEE 1584 method for three-phase open-air and enclosed studies less than 15 kV.
That said, it would be "nice" to have one approach to studies.
PostPosted: Sat Oct 05, 2019 7:17 pm
What is typical incident energy on a 120/240 service with Arc Pro
PostPosted: Mon Oct 07, 2019 5:38 am
You may consider the model described at http://arcadvisor.com/faq/single-phase-arc It has been implemented in ARCMASTER V1.0 software program for arc flash hazard analysis and labeling you can google online.
Michael Furtak, C.E.T.
