PostPosted: Tue Mar 10, 2020 9:32 am
I'm trying to figure out how to model a portion of this system. A contractor has recently installed four new motor feeders, and they all pass through a single disconnect enclosure. Each feeder has a 400A breaker at the MCC, and they each also have a 400A breaker in this new enclosure. I imagine the incident energy to be higher than the worst case for any single feeder, but don't think I should add them all together either. Has anybody dealt with something similar?
It looks more or less like this:
Code:
 Post subject: Re: Multiple disconnects in single enclosure
PostPosted: Tue Mar 10, 2020 12:35 pm
What software are you using? An arc on any one of the breakers would expand to include all the others. One way is to model the enclosure as a bus on the load side of all the breakers and then fault that bus. I use EasyPower so the bus would be set to ignore the main breakers, on Integrated method and that would give you the incident energy for that box.
PostPosted: Wed Mar 11, 2020 5:59 am
I am also using EasyPower.
That is how we approach most enclosures, but this equipment has several motors and control panels below it. I don't want to erroneously affect the IE at those panels. Maybe I'll run that as a scenario and see if anything changes significantly.
Thanks for the help.
PostPosted: Thu Mar 12, 2020 6:11 am
Yes you will have to do a separate analysis for the common enclosure and then do another for the equipment downstream with each feed as it is from the common enclosure.
PostPosted: Thu Mar 12, 2020 9:41 am
Does EasyPower have an easy way to do that, or would that have to be done manually?
PostPosted: Fri Mar 13, 2020 6:33 am
You would have to model it twice but that is not hard. One model would be with the single enclosure with all 4 breakers connected to a bus. The other with the system as it normally is. The single connected bus model would give you the incident energy for that enclosure.
Are all 4 breakers in the enclosure fed from the same bus or multiple different buses?
PostPosted: Fri Mar 13, 2020 7:27 am
They are all fed from individual 400A breakers on the same MCC bus.