It is currently Tue Oct 27, 2026 11:45 pm
 Post subject: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Mon Aug 24, 2020 8:11 am
Should a pad mount medium voltage distribution transformer have two separate arc flash labels; one for the high voltage compartment (Warning Label with high voltage and low incident energy) and one for the low voltage compartment (Danger Label with low voltage and high incident energy)? Should the information be combined into a single "Danger" label that lists the higher voltage and the higher incident energy?
 Post subject: Re: Labeling of MV Pad Mount Distribution Transformers
PostPosted: Tue Aug 25, 2020 11:39 am
Hello Mike,
Thank you for the feedback. Yes, I see in NESC Table 410.1 the arc flash incident energy is substantially less for Pad Mount transformers than what the short -circuit study was indicating. Would two labels still be needed due to the different voltages associated with the high and low voltage compartments of the transformer? Gary
PostPosted: Tue Aug 25, 2020 11:43 am
Hello Mike, I seem to have deleted the link you provided to the website in you post. Could you please post it again. Thanks
Gary
PostPosted: Thu Aug 27, 2020 6:37 am
If this padmount is owned by the utility, then there should be no labels on it as it falls under OSHA 1910.269 and in the forward, OSHA discusses that it does not believe that providing labels on transmission and distribution installations is feasible or effective. Even if the padmount is customer owned, it probably falls under OSHA 1910.269 because of utility like voltages and equipment.
Since the NESC is referenced, I would think this installation is under OSHA 1910.269 for arc flash
PostPosted: Thu Aug 27, 2020 3:57 pm
Thank you Barry and Mike. Excellent feedback and information. Gary
PostPosted: Wed Sep 02, 2020 5:31 am
If it was a substation transformer with side bushings and enclosures would you label the two enclosures differently?
PostPosted: Wed Sep 02, 2020 6:13 am
See above response regarding OSHA labeling for utilities.
PostPosted: Mon Oct 05, 2020 8:52 am
The sign should read:
Danger
Do Not Touch
Not Only Will This Kill You
It Will Hurt The Whole Time