Energized power lines on the ground pose a special hazard to the public (and electrical workers too)
This week's question is pretty simple. Have you ever seen an energized downed power line?
Yes
No
Stories are always welcome!
 Post subject: Re: Energized Downed Power Line
PostPosted: Mon Jun 07, 2021 7:18 am
Of course it is energized until isolated tested and grounded. On that basis, yes. Not only did I see it, I moved it bare handed. The line served my house, and was down on my driveway on the load side of the break, and I knew I was was not generating. Nearly a week before the line crew got out there.
A lot of good Samaritans out with chain saws that week. "Is that line deenergized?". "No, let the power company deal with it.
PostPosted: Tue Jun 15, 2021 6:32 am
Hi, yes I saw it once, our team worked on the road where the transmission line was de-energized, but well done they did what was required of them!
PostPosted: Mon Jul 05, 2021 8:14 am
At one of our Coal Mines we had 30 MVA Substation with a solidly grounded multi grounded 12 kV Wye system with feeder overcurrent ground relays.
At a remote location about five miles from the Substation, where the neutral was not carried, we had a downed phase conductor.
The rocks soil and copper fused into a mass before the relay operated.