It is currently Sun Oct 18, 2026 10:14 am



Post new topic Reply to topic
Author Message
 Post subject: Arc Flash Results
PostPosted: Mon Mar 10, 2025 7:23 am 

Joined: Wed Jun 12, 2024 5:19 am
Posts: 35
Hello,
I am working on this Arc Flash study for a company that wants the Incident energy levels below 4 cal.
I can figure out why these ones are so high.

I checked to make sure my data was correct. I'm not sure what to do now.


Attachments:
File comment: Here are the results for Panels SRL, ORP1, and Orp2.
AF Results for DPL1.jpg
AF Results for DPL1.jpg [ 270.86 KiB | Viewed 159740 times ]
File comment: This is the Data oneline
Panel DPL1.jpg
Panel DPL1.jpg [ 318.15 KiB | Viewed 159740 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Mon Mar 10, 2025 7:56 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
What is your arcing fault current vs your breaker trip curve? Those are some fairly long feeders. I suspect the fault current is "low" and arcing fault current in the short time region of the breaker curve, not the instantaneous region.

If so, that would increase breaker clearing time and therefore incident energy.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Mon Mar 10, 2025 8:00 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
Also, is that EasyPower? Should your most downstream feeders be 3-1/C, not 1-1/C?

Not an EasyPower user so not sure.

Attachment:
conductors.jpg
conductors.jpg [ 314.45 KiB | Viewed 159735 times ]

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Mon Mar 10, 2025 10:46 am 

Joined: Wed Jun 12, 2024 5:19 am
Posts: 35
Hey, I posted the Arc Fault from the bus.
And yes this is easypower. Do i have the conductors wrong? 3-1/C instead of 1-1/C?


Attachments:
File comment: Arc Flash Report.
Arc Flash Report.jpg
Arc Flash Report.jpg [ 104.64 KiB | Viewed 159729 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Mon Mar 10, 2025 11:11 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
Looks at your trip times. It is timing out per the 2 second rule. Those breakers with the higher incident energy aren't even tripping. That is why the IE is higher.

I've never used EasyPower but if I modeled this in SKM and it was 3 phase and I was using individual conductors (not a multiconductor cable, like a tray cable) then yes, I would have 3-1/C cables (A, B and C) or 4-1/C cables ( A, B, C, N). Not sure how it even calculates with only 1/C if EasyPower is the same.

EDIT: Also, I'm not sure what breaker is the protection, the upstream XT4N (for line side of main of the downstream panel) or the main breaker A2A in each panel. Depends on how you set up your study. If the XT4N is protection, some of those have adjustable instantaneous. If it is the A2A main breaker, they are fixed. If you run line side of main and your XT4N is adjustable, you might be able to set it to MIN and get a much lower IE.

If you want to set up a TEAMS meeting and share your screen I can try to help you if you like, although I don't know much about EasyPower.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Mon Mar 10, 2025 11:28 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
I looked at the curves with the XT4-N set to MIN. It looks like your energy is based on the A2A breaker tripping. At 1900 amps you are in the tolerance band of the breaker and it doesn't trip until well past 2 seconds. That is why you are timing out.

You could re-run your study to look at both the line and load side of the main and use the line side with the upstream XT4-N breaker tripping in the instantaneous region. That will get your energy down, I think, on the one that is 1900A arcing current set to MIN. The ones that are only 1200A, neither breaker trips quickly and you still have your "high" incident energy.

Attachment:
ABB CB.jpg
ABB CB.jpg [ 351.61 KiB | Viewed 159727 times ]

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Mon Mar 10, 2025 11:37 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
Attachment:
ABB CB min.jpg
ABB CB min.jpg [ 440.58 KiB | Viewed 159727 times ]

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Mon Mar 10, 2025 11:49 am 

Joined: Wed Jun 12, 2024 5:19 am
Posts: 35
Thank you. I am not available for teams meeting today.

Do you still use the 2 second rule if the panel is 208V?

Lower Voltages:
For voltages lower than 208V, some engineers use a shorter tripping time, such as 0.5 seconds, as the arc flash hazard is generally considered lower.

I found this on google.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Mon Mar 10, 2025 12:01 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
I do use the 2 second rule on 208V.

I'm not aware of the 0.5 second practice. I just may be ignorant though. That's not unusual, lol. IEEE does say there is a low risk for bolted fault currents under 2000A but your bolted fault currents are higher than 2000A.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Thu Mar 13, 2025 9:23 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 616
Location: Wisconsin
jsoar wrote:
I found this on google.


I have not found AI to be very good at technical/engineering topics. I prefer dedicated forums like this one. You might also try eng-tips, forums.mikeholt, or ones sponsored by software vendors.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Fri Mar 28, 2025 3:45 pm 
Sparks Level

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 75
bbaumer wrote:
Also, is that EasyPower? Should your most downstream feeders be 3-1/C, not 1-1/C?

Not an EasyPower user so not sure.

Attachment:
conductors.jpg

@bbaumer and also @jsoar: in EasyPower, "3-1/C" means three parallel conductors per phase in a single conductor cable configuration. So the first digit is how many (parallel) line conductors per phase, and the "X/C" is how many conductors in a cable configuration. So if I had a conductor run "1-3/C", that would be something in a 3-conductor cable assembly, such SO cable or something run in cable tray. A 3-phase circuit run showing "1-1/C" would be a standard 3-phase, one conductor-per-phase circuit. (note that neutral and ground are a separate tab and aren't addressed in that nomenclature)


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Results
PostPosted: Sat Mar 29, 2025 2:04 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
Makes sense. Thanks!

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 12 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883