| Author |
Message |
jsoar
Post subject: What are some ways to lower the Incident Energy for a Panel? Posted: Thu Sep 04, 2025 12:51 pm |
| Attachments: |
| Top |
bbaumer
Post subject: Re: What are some ways to lower the Incident Energy for a Pa Posted: Thu Sep 04, 2025 1:42 pm |
| Arc Level |
_________________ 95% Retired
| Top |
bbaumer
Post subject: Re: What are some ways to lower the Incident Energy for a Pa Posted: Thu Sep 04, 2025 1:51 pm |
| Arc Level |
| Top |
jsoar
Post subject: Re: What are some ways to lower the Incident Energy for a Pa Posted: Thu Sep 04, 2025 2:02 pm |
Hey, I used a Fused disconnect with FRS-R 175A. I was able to bring it down to 6.01. The customer wants to bring it under 4 cals if possible. I did play around and add an adjustable trip breaker. that did bring it under 4.
| Attachments: |
| Top |
bbaumer
Post subject: Re: What are some ways to lower the Incident Energy for a Pa Posted: Thu Sep 04, 2025 2:16 pm |
| Arc Level |
| Top |
bbaumer
Post subject: Re: What are some ways to lower the Incident Energy for a Pa Posted: Thu Sep 04, 2025 2:25 pm |
| Arc Level |
| Top |
bbaumer
Post subject: Re: What are some ways to lower the Incident Energy for a Pa Posted: Thu Sep 04, 2025 2:32 pm |
| Arc Level |
Run the report and look at your clearing time. I bet you are more than 2 seconds on the MCB. Also, I am having a hard time re-creating your model and getting 3000A of AFC with a 45 kva transformer at that %Z. I can only get like 3400A of bolted fault current. When I overlay the curves, you are barely in the instantaneous range of the breaker, if you even are. Attachment:
| Top |
bbaumer
Post subject: Re: What are some ways to lower the Incident Energy for a Pa Posted: Thu Sep 04, 2025 2:33 pm |
| Arc Level |
| Top |
bbaumer
Post subject: Re: What are some ways to lower the Incident Energy for a Pa Posted: Thu Sep 04, 2025 2:39 pm |
| Arc Level |
My AFC is much lower than yours. Same transformer, same cables. Not sure why. Mine times out at 2 seconds because I'm not in the instantaneous region of the MCB curve. Attachment:
| Top |
bbaumer
Post subject: Re: What are some ways to lower the Incident Energy for a Pa Posted: Fri Sep 05, 2025 1:57 am |
| Arc Level |
| Top |
Page 1 of 1
[ 10 posts ] |
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot post attachments in this forum