Post subject: Does all equipment have SCCR? Posted: Wed Jun 10, 2026 3:14 pm |
Im relatively new to studies learning as I continue school.
When modeling equipment and checking submittals and spec sheets, I often find it hard to locate the SCCR. Does all equipment come with an SCCR? If not, would you use a default of 5k or 10k?
Specifically, at this moment I am modeling some power line filters for a data center job. I dont see any ratings for the power line filters beyond voltage, current, and hertz
what do you do if SCCR is not listed?
| Top |
JBD
Post subject: Re: Does all equipment have SCCR? Posted: Mon Jul 06, 2026 9:29 am |
Joined: Mon Jan 18, 2010 11:35 am Posts: 616 Location: Wisconsin
I would use 5kA for hardwired devices. I think this is the default value that UL assigns to electronics like VFDs.
| Top |
jmoore284@gmail.com
Post subject: Re: Does all equipment have SCCR? Posted: Fri Aug 07, 2026 1:34 pm |
Joined: Fri Sep 28, 2018 7:32 am Posts: 63 Location: Sioux Falls, SD
Overcurrent protective devices will have an AIC. Assemblies (panelboards, switchboards, control panels, etc.) will have an SCCR. Per NEC it shall be marked...but this is not always done. For some equipment you can follow the guidance of the standards such as components listed in UL 508A Table SB4.1. This provides assumed maximum SCCR values for VFDs, motor controllers, breakers, and other items.
Equipment manufactured by big names like Schneider, Siemens, Eaton, etc. will always be marked.
| Top |
jmoore284@gmail.com
Post subject: Re: Does all equipment have SCCR? Posted: Fri Aug 07, 2026 1:36 pm |
JBD wrote: I would use 5kA for hardwired devices. I think this is the default value that UL assigns to electronics like VFDs. UL 508A Table SB4.1 lists the following for VFDs 0-50HP 5kA 51-200HP 10kA 201-400HP 18kA 401-600HP 30kA 601-900HP 42kA 901-1600HP 85kA