It is currently Sat Aug 29, 2026 12:07 am
 Post subject: Utility Modeling for arc Flash study
PostPosted: Wed Mar 26, 2008 9:46 pm
hi friends,
i am on the job of Arc Flash study of 1 industrial setup.
The given fault values contains max & min values & cooorosponding X/R ratio as mentioned below:
Utility Fault levels are given with following details:
Supply voltage : 440V Freq:50 hz
Utility Fault level :
3 phase :- Max : 13kA , Min : 8.6kA
1 phase :- Max : 8.8kA , Min :1.9kA
X/R Ratio :
3 phase :- Max : 3.62 , Min : 0.329
1 phase :- Max : 3.31 , Min : 0.22
So, my questions is, how to model the utility for Arc Flash studies?
Is it required to model two utilities with 1 with max fault level & 1 with min fault level & corrosponding X/R ratio ; one is operating at a time.
Please advise?
PostPosted: Fri Mar 28, 2008 3:19 pm
Your software may allow you to model the system for both scenarios without requiring you to model the system twice. If you use the IEEE 1584 equations, there is a built in (reduced fault current) check that will evaluate 100% and 85% of fault current. If you model both the high and low estimate at both 100% and 85%, you will have a sufficient analysis. I don’t know if this is an option in all available software packages but this is an option in the Easy Power software.
