It is currently Mon Aug 31, 2026 2:22 pm
 Post subject: NFPA 70E and Electric Utilities
PostPosted: Thu Sep 13, 2007 5:48 am
Does 70E apply to utilities? If I am reading Article 90.1 (B) (5) it does not. However, it seems many utilities are pro active about arc flash studies. What is driving this? Liability?
PostPosted: Thu Sep 13, 2007 11:43 am
NFPA 70E and Utilities
I believe it is a catch 22. Utilities are bound by OSHA which references 70E then 70E has an exemption for electric utility transmission, generation and distribution. Therefore most utilities that I know are attempting to follow 70E as best as they can even though the nature of the business does not alllow working electrically safe very often. I am sure someone is also thinking about liability also.
PostPosted: Thu Oct 18, 2007 8:01 pm
I have worked on both utility and non utility systems and my opinion is that NFPA 70E would stop most utilties from performing the work the way they have for the past 100 years.
PostPosted: Mon Nov 12, 2007 1:43 pm
OSHA clarifies that all referenced material is ONE but not the ONLY way to meet the intent of providing a safe woring environment. The Utilities have been far ahead of NFPA 70E with their own safety practices and standards and have the numbers to back it up. They can continue their practices with the consent of their legal departments and remain square with OSHA. (IMOW of course.)
PostPosted: Sat Jul 12, 2008 11:16 am
Don't utiities follow the NESC and would't this be in place of 70E or must they comply with both?
Joe
PostPosted: Sat Jul 12, 2008 11:58 am
For transmission work yes I agree, but distribution level they dont take any arc flash precautions, not in my area anyway and not the last place I lived either. We see utilities do all sorts of stuff hot without any PPE all the time, just last week I saw a guy repairing a cable termination (Replaceing mounting bolt for B phase that had broke of and was single phasing transformer).
I imagine this will all change (Slowly, like it has in our world) when the NESC adopts parts of the 70E, which they are in process of doing now.
PostPosted: Sat Jul 12, 2008 1:23 pm
Electric Distribution System Live Work
One might find it surprising but for many 15 kV distribution systems out there using inst trip attachments on feeder breakers, even at high levels of fault duty the IE can be less than 1 for the primary system. Many systems worst case are still less than 4 cal. Many linemen are wearing FR clothing of at least 4 cal while most would be 7 to 8 cal. Since we don't deal with the arc in a box issue, the energy is not totally focused on the lineman. Once you get to 25 and 35 kV it can get a little worse, but with proper relay settings it is still not an issue....just for info.
Alan
PostPosted: Sat Jul 12, 2008 10:15 pm
Its not the lines I worry about, it is the padmount tansformers, this guy I saw last week was on the 480V side of the padmount (Long clearing times and high fault currents) replacing a broken connection while energized. Just jeans and a T-shirt.
PostPosted: Sun Jul 13, 2008 4:48 am
Padmounts
I do think that if there are significant issues, the pad/ground mounted equipment is where they will be.
PostPosted: Mon Apr 06, 2009 11:05 am
Generating Facilities
Generating facilities are technically categorized as "utility" entities. However, their environment is much more industrial (typical switchgear enclosures, lots of low voltage equipment, etc.). Does anyone know of any cases where a generating facility, for liability purposes, specifically avoided citing NFPA 70E in their arc flash policy?
Are these facilites technically exempt from NFPA 70E?
PostPosted: Mon Apr 06, 2009 12:29 pm
IMO yes they are, article 90.2 (B)(5)
90.2 Scope
B - Not covered
5 - installations under the exclusive control of an electric utility where such installations
c- Are on property owned or leased by the electric utility for the purposes of ..generation..of electric energy
PostPosted: Mon Apr 06, 2009 1:18 pm
Generating Facilites and NFPA-70E
Thanks. So despite being technically exempt, is it typical for generating facilities to use NFPA-70E as the means for compliance with OSHA and NESC requirements? Any examples?
PostPosted: Mon Apr 06, 2009 3:19 pm
I have not seen many utility owned generation facilities follow the 70E, but I have seen many commercially or privately owned generation facilities following the 70E.
PostPosted: Mon Apr 06, 2009 4:59 pm
Zog is correct, but make sure you understand the exemptions in 70E. Just because it is generation does not exempt it! It must meet the exemption requirements to fall under the NESC. Is this a utility owned, maintained, and controlled installation?
Alan
PostPosted: Tue Apr 07, 2009 5:26 am
I haven't heard any one reference article 410 in the NESC yet. 410 talks about assesing for potential arc exposure. If the arc exposure is greater than 2 cal/cm2 then they need FR ppe. It even goes on to use the word arc hazard analysis and give specifics that should be considered in the analysis.
Either the guy at the transformer calculated that the hazard was under 2 cals or he was out of compliance.
PostPosted: Tue Apr 14, 2009 9:08 am
Alan
The generating facilities are large base load units, but are privately owned. What other source(s) describe exempt entities besides that cited by Zog above? Thanks.
PostPosted: Tue Apr 14, 2009 9:35 am
I only quoted part of the 70E scope, read it all. 90.2(A)(1) Implies that anything privatly or public owned is covered, unless noted in the exceptions. My interpretation is a private owned generation facility would be covered by the 70E. You can also reference OSHA 1910.269.
PostPosted: Tue Apr 14, 2009 10:27 am
As in my previous post:
Appears that you need to follow 70E.
Alan
PostPosted: Tue Apr 14, 2009 12:04 pm
We are using IEEE-1584 as the calculation method (within SKM) to determine compliance with NESC for our municipal utility clients' generating facilities. We use ArcPro for overhead utility systems.
PostPosted: Tue Jun 02, 2009 7:45 pm
NFPA 70E does not exempts TDG. It exempts electric utilities. Many plants have distribution systems that fall in the 1910.269 and under NFPA 70E. There are also many facilties that co-gen but are not electric utilities and they all are under NFPA 70E.
As far as utilities following 70E, they are not exempt from the General Duty Clause under OSHA rules and OSHA says since NFPA 70E is a industry standard, that they will use it in evaluating whether the utility did everything they could to protect the employee. With all the electricl utility employees getting killed every year I can see where the legal departments are going to win out even though 70E is not a legal standard. Strange though, the fine for failing to report the transformers in the yard with PCB's is 100 times higher than having an employee get killed not wearing PPE.