It is currently Wed Sep 09, 2026 2:21 am
 Post subject: Utility data-incorrect?
PostPosted: Fri Aug 12, 2011 4:03 pm
I was working on Short circuit study involving utility supply.
I confirmed with utility representative several time but All i received was following data...I do not trust this data, Please help me understand how can this be right data.
System Positive Sequence Impedance:
R= 7.41 ohms
X= 6.42 ohms
System Zero Sequence Impedance:
R0= 9.28 ohms
X0= 20.38 ohms
The X/R ratio in positive sequence is less than 1. Is it possible in any case.
I can not get any relaible dat after digging many times now.
Even in zero sequence case the ratio is hardly around 2.
the 3 ph Symmetrical short circuit duty is provided as 735 A
and single line to ground : 526 A
circuit base voltage: 12470 V
Thank you
PostPosted: Mon Aug 15, 2011 11:44 am
It certainly appears that something is incorrect. A low X/R is not that unusual if you have a low short circuit current since often it means you are at the end of a long small mostly resistive conductor.
However this is usually at low voltage. MV tends to be a bit more inductive. In any case, the short circuit current seems very very low. Is this on the end of a long line in a remote area? I wonder what kind of voltage drop they have based on such data.
It sounds like you should be asking them again to clarify the data.
PostPosted: Tue Aug 16, 2011 8:21 am
The voltage drop can be cured with regulators. Common construction in rural areas; run distribution lines long distances and insert a regulator when the voltage becomes unacceptable. For smaller conductor sizes (2/0 Al or #2 Cu), the resistance will exceed the reactance even at medium voltage.
Where is this installation, and how far away is the feeding substation?
PostPosted: Wed Aug 17, 2011 11:55 am
While this seems very low, I encountered SC value of 980A on a 12.5 kV system. After some discussions with the utility rep, it turned out it was a case of too small a substation TR, with too high an impedance, located too far away, feed with too small conductor.
It would be a good idea to see if the utility rep can give you some of the parameters above. You can do a quick calculation to see if this is in the ball park.
Bob Ragsdale, P.E.