It is currently Mon Aug 31, 2026 11:26 am
 Post subject: Which equipment needs labels per NFPA 70E 2012?
PostPosted: Mon Jan 09, 2012 7:20 pm
The new NFPA 70E-2012 describes very clearly the type of equipment that needs arc-flash labels. I have three questions:
1. Industrial Control Panels.
I have seen a good number of comments and presentations from label manufactures and other that non-fused disconnect switches and fusible disconnect switches qualify as Industrial Control Panels, and therefore, we must calculate the incident energy and place labels on them.
I have read the NEC 70-2011 definition of Industrial Control Panel and is still not clear for me if the fused or un-fused disconnect switches belong to this classification of equipment.
2. Busways.
This very popular distribution type equipment does not appear on the list. Do we need to place arc-flash labels on busways?
3. Switchgear (different to switchboard) are not mentioned. Is it your understanding that, according to the strict wording of NFPA 70E 2012, switch-gears are not required to have a label?
Do not misunderstand my question. I do place labels on fusible disconnect switches, busways, and switchgear equipment because of safety. But I am looking to increase my understanding of the strict interpretation of the words of the NFPA 70E 2012.
PostPosted: Tue Jan 10, 2012 7:04 am
Anything that requires adjustment, maintenance, or servicing while energized.
PostPosted: Tue Jan 10, 2012 9:43 am
NFPA 70E requires labeling for electrical equipment "such as switchboards, panelboards..." When the term "such as" is used, it is not exclusive. You can't surmise that if a piece of equipment is not listed that it does not require a label.
PostPosted: Mon Sep 17, 2012 1:06 am
The NFPA 70E listings have always emphasized on strict labelling of electrical equipment. This is an essential safety standard and must not be overlooked at all. Switchboards and panel-boards were stated as examples because these are mostly left without labels.
